Hmm... that's not the case according to about 1000 posts on Will Prowse's DIYsolarforum:The batteries will have built in battery management systems, so it will work fine. You do not need to do anything special. You just give a constant 14.4 voltage and the batteries manage the charging internally.
Hmm... that's not the case according to about 1000 posts on Will Prowse's DIYsolarforum:
Vehicle Mounted Systems
RV's, Vans, Trucks and More! Typically 12v, and 100-1000w, but the limits are endless!diysolarforum.com
In fact, a constant 14.4 volts is NOT the optimal charge schedule for most all LFPs, no matter what BMS they have. Each manufacturer specifies voltages for bulk, absorbtion, float, and storage charging, and they are not the same for all LFPs. Some like Renogy have an odd number of cells that makes these voltages significantly different from others. And a good dc to dc charger can be set to these voltages for optimal charging.
Any disparity in cable length or resistance between the batteries and charger, or batteries and load, will cause one to charge faster and discharge faster. Different cable temps between bed and engine bay will cause different resistance also. This makes one battery finish bulk charging and go into float before the other. This will cause balance issues that can significantly decrease battery life. Yes, over time without use they can self balance, but exact same cable lengths is a critical design requirement.
Putting both batteries physically together will remove most all of these issues and let you charge with one charger. Or better yet, buy a 200Ah battery, then you just have one BMS to deal with.
Great! You should tell all the manufacturers of LFP battery chargers, and dc to dc chargers--Victron etc-- that they're wrong too, and that their products aren't needed and pointless! Will Prowse has 10 videos or so about setting up parallel LFP battery banks and cable length issues, you should let him know it's all b.s. too!You seriously have no idea what you are talking about. The batteries control the charge and cell balancing internally. It matters not what happens outside.
The short answer is that two batteries in parallel act as one battery. So your charger only needs one output.
The broader question is the wire distance implicit in your setup.
-- The batteries in parallel should be charged (and discharged) "diagonally." That means that the charger and the loads are wired to the positive of one battery and the negative of the other. This makes the draw on the batteries more even.
-- The paralleling wires between the batteries will need to be big enough to sustain your biggest draw without much voltage drop. So you will need to know what that is and size your wires accordingly. If not, your 100Ah battery becomes effectively smaller.
-- The same wire sizing issue will arise with the Victron - the wires have to be big enough to carry the rated output over the distance without significant voltage drop.
The short suggestion is put them both in the bed - things will be much neater and easier.
Since we are spending yer money ...I thought about putting them both in the bed, but the unused space under the hood (some models of F-250 have 2 batteries from the factory) is really agitating my OCD. That said, I do want to mount the battery in the bed right up against the cab, so at least the wire run wouldn't be as long as if I was running it from the tail end of the bed.
@DaveInDenver Hugely helpful and confirms my very uneducated suspicion. I have an uneven draw issue with my two battery setup, although I suspect it may be due to a bad BMS. Could also be because of the crappy OG Northstar wiring setup, which consists of wire nuts and inline common 30 blade fuses. Pure garbage. I'll be adding a DC/DC charger (alternator) and redoing the system with bus bars and appropriate fuses and accounting for future solar. These are all 100ah SOK heated units. First two are two years old and 2nd two are new. Old units have less than 50 total cycles. Any special consideration you recommend for mixing old and new batteries?@DirtWhiskey the normal two battery cross style expanded to four is alright and is the minimum but the Victron topology is best.
The compromise comes down to cost and access. If the layout makes the middle connection difficult to achieve feeding across has benefit over the long branch parallel, which is guaranteed to wear the bank out unevenly and over time end up with wildly unequal SOC.
Also Iota is showing theoretical in their graphic, you may not see quite this much difference in outside vs inside on method 1 while method 2 won't be perfectly equal. Either is acceptable in practice, which generally suggests no more than 15% difference between the best to worst in a bank.
Also remember that both charger and load have to be wired in these ways to really have the best chance to stay balanced.
View attachment 849449
View attachment 849445
View attachment 849446
Doesn't the DC DC charger prevent the batteries from accepting too much charge and overloading the alternator and also keeps the charge voltage in the acceptable range?To wire multiple batteries in series, I prefer the "star" method.
The positive from each battery goes to a common connector using identical cable of identical length. Same with the earths. Each battery sees exactly the same resistance this way.
In my view, the only point in using a DC-DC charger is if the voltage drop in the too small cables is excessive. I charge from my alternator directly and did so with AGM batteries and now with 320Ah of prismatic LiFeO4.
Cheers,
Peter
OKA196 motorhome