I don't know if we disagree or not, but most consumer-level MPPT controllers still use techniques that will favor higher voltage, particularly when temperatures are elevated and during non-ideal irradiance. The controller efficiency will also decrease as current increases, you know that dwh, conduction and switching losses go up. So your example of 17V/6A -> 13V/8A vs. 34V/3A -> 13V/8A may be more like 17V/6A -> 13V/7.8A vs 34V/3A -> 13V/7.9A with 3% power supply losses.
I do concede it is somewhat inconsequential, since as you point out, it's such a low power system that losses are proportionally low, too.
But also to mention, you also don't want to switch from buck to boost, that will further reduce converter efficiency. You want the panel array (assuming at high temp) to stay well above the charging voltage. The P-V curve favors following the voltage as far right as possible when the panels are used in the summer and at less than 100% irradiance.
The difference in cabling, I dunno, it's obviously not tremendous but I think it's important. Since 10AWG is about 3 milliohms per meter, 50' is about 46 milliohms. For a 170W panel a change from 34V/6A to 17V/12A means you'll lose a couple of watts more in heating the cable. The controller doesn't care, 170W is 170W, so as long as the expected cold temp max voltage is not exceeded (which is 75V for the SunSaver MPPT) there's no reason not to run a higher voltage, letting current be what it is (assuming the panels are all fairly closely rated).
My point is all these little 1% here, 3% there losses do add up system-wide even for small portable systems.
I do concede it is somewhat inconsequential, since as you point out, it's such a low power system that losses are proportionally low, too.
But also to mention, you also don't want to switch from buck to boost, that will further reduce converter efficiency. You want the panel array (assuming at high temp) to stay well above the charging voltage. The P-V curve favors following the voltage as far right as possible when the panels are used in the summer and at less than 100% irradiance.
The difference in cabling, I dunno, it's obviously not tremendous but I think it's important. Since 10AWG is about 3 milliohms per meter, 50' is about 46 milliohms. For a 170W panel a change from 34V/6A to 17V/12A means you'll lose a couple of watts more in heating the cable. The controller doesn't care, 170W is 170W, so as long as the expected cold temp max voltage is not exceeded (which is 75V for the SunSaver MPPT) there's no reason not to run a higher voltage, letting current be what it is (assuming the panels are all fairly closely rated).
My point is all these little 1% here, 3% there losses do add up system-wide even for small portable systems.