Better wire for solar panels -> charge controller?

verdesardog

Explorer
Measurement error.

PV to meter to pv. That is a different circuit than the pv to battery to pv circuit and operates at a different voltage (no battery in that circuit, less resistance, higher voltage) than the pv to battery to pv circuit.

Since you are measuring the voltage of a short, low resistance circuit, you'll see the full *potential* of the pv.

But that has nothing to do with what is happening over on the other circuit where the battery is.

In other words...easy to fool yourself that way.


Are you disputing this schematic? .02 ohm wire with 10 amp flowing will cause a .2 volt drop across the + and - wire.

Untitled-110.jpg


Because if you are then there is no use talking to you any more.
 

rossvtaylor

Adventurer
Hi all... I hesitated to post this, because I didn't want to sound like I was being contrary to some of the excellent points being argued. But... <said sheepishly> nobody has pointed out that voltage rise may be a factor in some of the measurements here. Now, I'm not a solar expert by any means... my background, and current full-time career, is in wind energy and mechanical generators operate differently than PV arrays, I know. But I regularly see issues with voltage rise in lines, where the cabling is undersized. Voltage drop occurs where there is a load at the end of a line, which has resistance (as they all do, unless super cooled like was pointed out). SO, your 1800W heater load will cause a drop in voltage at the load/heater end of the line, as compared to the voltage measured at the line/source end.

But, in a generator configuration the opposite happens. People who haven't seen this happen have a hard time picturing it, so I use a water pump example. If the hose it too small, as the pump runs it can raise the pressure on the pump end of the system. The same happens with inverter or generator sources, as they push energy through a line... there will always be some voltage rise, due to line resistance. The goal is to make it manageable, so inverter and wind generator manufacturers have tolerance limits. It's even built into the UL 1741 and IEEE specs, so that systems don't shut down inappropriately. I know of one popular system where the tolerance is 2% but some are 5%. And, I've personally had to diagnose and resolve issues with systems (installed with wire too small) where the inverters shut down because they were "pumping" energy into a wire which was too small for the length of run... voltage would rise above the threshold limits and the system would shut down.

People don't talk much about voltage rise, because we're used to working with loads (that cause a drop, because we're measuring at the load end). But it happens in the opposite direction with generation systems... at least the ones I'm familiar with. Having said that, I have NO idea if PV output can work this way. But if you're working with charge controllers (on the DC side) or inverters (on the AC side), then this is a very real and measurable phenomenon.
 

verdesardog

Explorer
Even if there is no controller there will still be less voltage at the battery than at the solar panel. (No one is talking about what is happening inside the controller PWM or MPPT, we are talking voltage drop across the wires going to the controller)

Untitled-211.jpg


In this case current will be limited buy the difference in voltage of Pv and Bv and resistance of the circuit. Bv will be lower than Pv.
 
Last edited:

verdesardog

Explorer
So here's another way of looking at it:

Untitled-39.jpg


As long as there is current flowing through a resistor there will be a voltage developed across that resistor which will subtract from the source voltage. There is no way of getting around the laws of physics. If the controller is an MPPT it can output more current than the pv is supplying but the power is the same as what the pv is outputting minus power lost due to resistance of the wires. P=IE. There will ALWAYS be a loss of power due to resistance of the wires.
 
Last edited:

4x4junkie

Explorer
Measurement error.

PV to meter to pv. That is a different circuit than the pv to battery to pv circuit and operates at a different voltage (no battery in that circuit, less resistance, higher voltage) than the pv to battery to pv circuit.

Since you are measuring the voltage of a short, low resistance circuit, you'll see the full *potential* of the pv.

But that has nothing to do with what is happening over on the other circuit where the battery is.

In other words...easy to fool yourself that way.

Well I guess I do have to give you credit for your persistence in not making sense...
Too bad you're completely wrong on this one (which I find very odd too, because most of your other posts always seem to be dead on the money :confused: ).

rossvtaylor's post is also dead-on accurate, and PV systems certainly are subject to voltage rise too (which was exactly the example I gave about a panel's operating voltage potentially rising above it's Vmp). It all comes from too much resistance in the wiring (too-small gauge conductors) and of course this will always diminish performance.


I faded out right about the first mention of Vmp...
Measuring voltage as described, one is seeing higher voltage at the 'source', and lower voltage at the output of the charge controller. This is normal of any voltage regulator, nevermind conductor resistance or controller type.

While a PWM controller is in the bulk charging phase, you should see nearly the same voltage on the input (PV) side of the controller as the output (battery) side. This is because a PWM controller simply passes the PV current straight through the controller to the battery during Bulk charging. Once the controller go into the Absorb phase, then you may start to see the voltage on the PV side rise as it begins to pulse the circuit on & off. My post is specifically about while it is in the Bulk phase (same as if the PV panel is connected directly to the battery).
 

verdesardog

Explorer
Well I guess I do have to give you credit for your persistence in not making sense...
Too bad you're completely wrong on this one (which I find very odd too, because most of your other posts always seem to be dead on the money :confused: ).

rossvtaylor's post is also dead-on accurate, and PV systems certainly are subject to voltage rise too (which was exactly the example I gave about a panel's operating voltage potentially rising above it's Vmp). It all comes from too much resistance in the wiring (too-small gauge conductors) and of course this will always diminish performance.




While a PWM controller is in the bulk charging phase, you should see nearly the same voltage on the input (PV) side of the controller as the output (battery) side. This is because a PWM controller simply passes the PV current straight through the controller to the battery during Bulk charging. Once the controller go into the Absorb phase, then you may start to see the voltage on the PV side rise as it begins to pulse the circuit on & off. My post is specifically about while it is in the Bulk phase (same as if the PV panel is connected directly to the battery).

So let me get this straight ... you are saying there is something magic in a pv system that makes no voltage developed across a resistor (the wire) when there is current flowing through it? YOU ARE WRONG.
 

4x4junkie

Explorer
So let me get this straight ... you are saying there is something magic in a pv system that makes no voltage developed across a resistor (the wire) when there is current flowing through it? YOU ARE WRONG.

Did you quote the wrong post?

Or maybe you misunderstood me... I was referring to the voltage being the same at the input terminals of a PWM controller as at the output terminals of the controller.

I already agreed with you and said if you measure at the panel itself, the voltage will always be higher than at the battery (or the battery will be lower than that of the panel, whichever way you want to put it).
 

dwh

Tail-End Charlie
Good god...

I've said this before many times in many other posts. But I'll say it again and anyone who fails to understand it is not worth trying to educate.

A CIRCUIT IS A LOOP.

Anyone who thinks voltage drops from one end of a loop to the other end of the loop just doesn't understand that A CIRCLE HAS NO ENDS.
 

dwh

Tail-End Charlie
And...

MEASURING THE VOLTAGE THROUGH A SHORT CIRCUIT THAT BYPASSES PART OR ALL OF A LONG CIRCUIT DOES NOT TELL YOU THE VOLTAGE OF THE LONG CIRCUIT.
 

dwh

Tail-End Charlie
Pv
Wire
Battery at 13v
Wire
Pv

A loop.
What is the voltage of the loop?
13v.
Everywhere.
Around THE ENTIRE LOOP.

How much is the resistance of the wire causing the voltage of the loop to drop?

None. The battery is regulating the voltage of the loop at 13v.
 

verdesardog

Explorer
Don't be so dense. You guys are all wrong! If there is no difference in potential (voltage) there will be NO current flow. How difficult is that to understand?

AS far as crimping or soldering, it all depends on the terminals that you are using.
 

dwh

Tail-End Charlie
Of course there is a higher potential and that will cause CURRENT to flow.

But that has nothing to do with regulating the VOLTAGE on the charging loop.

Current will flow...regulated at 13v and rising as the battery voltage rises.

What is the definition of potential?
 

dwh

Tail-End Charlie
Also...

The difference in potential is NOT "from solar to battery". It's "from solar+ to solar-".

(Actually thats backward...electrons flow from neg to pos. Blame that goof on Ben Franklin.)
 

verdesardog

Explorer
Also...

The difference in potential is NOT "from solar to battery". It's "from solar+ to solar-".

(Actually thats backward...electrons flow from neg to pos. Blame that goof on Ben Franklin.)

In America the convention is current flows - to +, Europe the conventional thinking is + to -. How does it get from solar - to solar + ? through the battery otherwise there will be no current flow through the battery to charge it. What makes it flow? Difference of potential, voltage. Consider two sources in parallel, if they have the same voltage there will be no current flow.

Maybe you need to go measure the voltage of your system at the output of the solar panel and the input to the controllerwhen it is running 10 amps and see for yourself. Of course since we are talking voltage drop in the wires it will be a very small voltage. Any decent volt meter should be able to show millivolts which is what you should expect to see. This whole thread started out discussing voltage drop across the wires which has nothing to do with output of the controller or how different controllers work.
 