This was designed with lead/acid 6V duracell battery bank, right? So if there is 220AH total, how much of that capacity is usable? I thought i read not to go past 50% use from a lead acid, so around 110AH usable?
The 50% hard line is mostly a myth. With true deep cycle batteries you can discharge down to 80% without a major impact on *total lifetime* AHs delivered.
Lead Acid 50% DOD Limit; Rule or Myth
Greetings. I have a fair amount of experience with lead acid deep cycle batteries in vehicle and PV systems (fork lifts, golf carts, small EVs, etc). I have seen/heard the following truism for as long as I can remember. "Don't discharge your lead acid batteries below 50% ever" I believe...
expeditionportal.com
For easy math assume a battery delivers 10,000 AH over its life. If you discharge a 100AH battery down to 50% you will get about 10,000/50=200 cycles. If you discharge to 80%, you will get 10,000/80=125 cycles. Te reality is not quite linear, so it would be something like 220 and 110 cycles, but the total AH delivered would be close. The biggest issue is being able to recovery the discharged AHs. Lead acid does not like to sit partially charged. At least once every 2-3 cycles (or 1-2x a week) the battery must be charged to a true 100%, this takes 8 or more hours at the correct voltage. Ideally this would happen after every deep discharge, but reality gets in the way.
Those golf cart batteries can supply 150A at a reasonable voltage drop for the top 50%. If you drop below 50% SOC, and try to pull 150A, the voltage may drop too low for the inverter.
The first step in an electrical system is to make a rough budget for AHs or watt-hours. This means a tally of all the consumers, their real world current or watt consumption, and then how often they are used. Do the same for charging if available. From there you can start refining whats possible.