Blue Sea ACR and DC to DC Charger?

Alloy

Well-known member
If one really wanted/had to go DC-DC is there a reason why 2-3 couldn't set up in parallel?
 

DiploStrat

Expedition Leader
DC-DC chargers have their place - anywhere the standard regulator/alternator cannot provide the correct voltage or needs extra protection from overload. Typically, this translates to anywhere the starter and camper/house batteries are very different chemistries. (Generally, flooded, sealed, and absorbed glass matt batteries all qualify as the same.)

But remember, the DC-DC charger cannot "make" current - it is still getting it from the vehicle's alternator. In fact, a DC-DC charger typically gives up amps to get volts.

These devices are just tools, not magic.

Lawyerly weasel words added because there are ALWAYS exceptions out there. ;) But really, this stuff is not hard to follow at the consumer level.
 

john61ct

Adventurer
None of the Renogy units allow for user custom adjustment of setpoints.

I know the Sterling B2Bs have always, and I understand Kisae do as well.

Sterling is def OK with stacking their units in parallel, dunno about any others.
 

Rbertalotto

Explorer
None of the Renogy units allow for user custom adjustment of setpoints.

Not sure if you are referring to the RENOGY dc to DC chargers. The one I have has DIP switches to set the setpoints.....
 

john61ct

Adventurer
Not sure if you are referring to the RENOGY dc to DC chargers. The one I have has DIP switches to set the setpoints.....
Yes, giving just a limited set of canned profiles to choose from, as is the norm.

I'm talking about **user custom** adjustment, so if I want my GEL bank to get 13.3V at Float but 14.2V for Absorb/CV

Or adjust my LFP Absorb up from 13.8 to 14.1V

like that. . .
 