AC units have whats called the coefficient of performance (COP). No matter what you do, most units are probably going to run between 2.5 and maybe 4 on the high side. This means for every watt of electrical power, they remove 2.5-4 watts of heat from the cabin. Cheap units will likely be near 2 in hot conditions.
For a 2.5 COP unit, 1kw of input power will yield 2.5kw of cooling. That's about 8530 BTU/hr.
So moving to DC native is not going to magically make the system use little power. It will remove a 10-15% efficiency loss, but that may be negated by a lower COP in the new unit. Its not a simply task to work out what will happen.