datasheet for panel in question
datasheet for mppt 100/30 in question
panel datasheet says shortcircuit current is 8.37A
optimum current and voltage are 7.92A and 20.2V respectively
mppt datasheet says rated for 30A and max PV array short circuit current is 35A and anything over could damage it
8.37 x 4 = 33.48A which is less than 35A
so does that mean i could wire 4 of these panels in parallel without damaging the mppt 100/30?
I think what's confusing me is converting from the operating PV voltage of around 20-22v to the battery which is somewhere around 14.4v. On the 160w panel, 160w / 20v = 8A so that makes sense. but If I convert that to 14.4v, then 160w / 14.4v = 11.1A and if I put 4 panels in parallel that would be 44.4A (43.5 at 98% efficiency) leaving the MPPT going into the battery, right? 43.5A exceeds both rated and max current of 30 and 35A. But since the datasheet says "max PV" i assume i can do 4 panels and that the output side can handle it? Or should I drop to 3 panels? (24A @20v in and 33.3A @ 14.4v out?)
how many amps are going into my battery per panel? 8A? or 11A?
datasheet for mppt 100/30 in question
panel datasheet says shortcircuit current is 8.37A
optimum current and voltage are 7.92A and 20.2V respectively
mppt datasheet says rated for 30A and max PV array short circuit current is 35A and anything over could damage it
8.37 x 4 = 33.48A which is less than 35A
so does that mean i could wire 4 of these panels in parallel without damaging the mppt 100/30?
I think what's confusing me is converting from the operating PV voltage of around 20-22v to the battery which is somewhere around 14.4v. On the 160w panel, 160w / 20v = 8A so that makes sense. but If I convert that to 14.4v, then 160w / 14.4v = 11.1A and if I put 4 panels in parallel that would be 44.4A (43.5 at 98% efficiency) leaving the MPPT going into the battery, right? 43.5A exceeds both rated and max current of 30 and 35A. But since the datasheet says "max PV" i assume i can do 4 panels and that the output side can handle it? Or should I drop to 3 panels? (24A @20v in and 33.3A @ 14.4v out?)
how many amps are going into my battery per panel? 8A? or 11A?