While your messing with that Plexiglas door, you might want to consider this. Propane storage is supposed to be
completely isolated from the cabin area in case there is a leak or the pressure relief valve vents. And, it's just common sense you can't have any electrical equipment mounted in the same compartment as the tanks either.
As per
NFPA 1192 Standard on Recreational Vehicles 2005 Edition (I checked the current version which is 2015, and they are the same, but I can't copy and paste from that one.
5.2.3 Location of Propane Containers.
5.2.3.1 Propane containers that do not meet the provisions of 5.2.3.2 shall not be installed nor shall provisions be made for installing or storing any propane containers, even temporarily, inside any recreational vehicle.
5.2.3.3 Propane containers with their control valves shall be installed in compliance with one of the following:
(1) Mounted in a recess or compartment other than on the roof that is
vapor resistant to the inside of the recreational vehicle.
5.2.3.4 Containers
shall not be mounted on the exterior of the rear wall or the rear bumper of the vehicle.
5.2.4 Securing of Propane Containers.
5.2.4.1 Containers shall be secured in place so they do not become dislodged when a load equal to eight times the container's filled weight is applied to the filled container's center of gravity in any direction.
5.2.6 Ventilation of Compartments Containing Propane Containers.
5.2.6.1 Compartments shall be ventilated at or near the top and at the extreme bottom to facilitate diffusion of vapors.
5.2.6.2 The compartment shall be ventilated with at least two vents, each having an aggregate free area equal to at least 0.5 in.2 for each 7 lb (3.23 cm 2 per 500 g) of the total propane fuel capacity of the maximum number of the largest cylinders the compartment can hold.
5.2.6.3
If the lower vent is located in the access door or wall, the bottom edge of the vent shall be flush with the floor level of the compartment.
5.2.6.4 The top vent shall be located in the access door or wall, with the bottom of the vent within 12 in. (305 mm) of the ceiling of the compartment.
5.2.6.5 Vents shall have an unrestricted discharge to the outside atmosphere.
5.2.6.6 Doors or panels providing access to valves shall not be equipped with locks or require special tools to open.
Here is the full instruction:
http://hamyarenergy.com/static/fckimages/files/NFPA/Hamyar Energy NFPA 1192 - 2005.pdf
I realize we are not building these things to be sold on the open market, and they will not be inspected or required to meet any particular building codes, however my philosophy is to follow the existing codes as closely as possible, especially the safety codes. People much wiser that we have put many thousands of hours of research and testing into writing these codes, so it's probably worth following them as closely as possible.