It looks like even with 13.5A* running through a 3ft length of #10 wire there's an unacceptable voltage drop (around 4v) so the split wire is not going to happen unfortunately.

Bolting it could be an option. What I would ideally do with the SB is install it in a flush mount box in the side of the bed. I've seen plenty of photos of them, but have no idea what they're called to search for them!

*27A for a 20A renege DC/DC, lower than I'd want but acceptable.
 

dreadlocks

Well-known member
~0.75% voltage drop with 3ft of 10awg on 15A, well under the 1-3% range most shoot for.

if 12v in, 11.9v out.
 

Amp34

Member
o_O

I did the calculation about 5 times because it didn't make sense. Once more after reading I'm wrong and I get your answer. Still not sure what happened there...

Also found this:


A protected flush mount socket for the SB50 connection. Unfortunately only comes in the 50, which takes up to #6 wire. Too much wire to strip off a #4 to fit it in? I'll have to take around 1/3rd off, but could compensate by soldering it in. Alternatively I could just stick with a 20A DC-DC and run 6AWG the entire way.
 

Alloy

Well-known member
o_O

I did the calculation about 5 times because it didn't make sense. Once more after reading I'm wrong and I get your answer. Still not sure what happened there...

Also found this:


A protected flush mount socket for the SB50 connection. Unfortunately only comes in the 50, which takes up to #6 wire. Too much wire to strip off a #4 to fit it in? I'll have to take around 1/3rd off, but could compensate by soldering it in. Alternatively I could just stick with a 20A DC-DC and run 6AWG the entire way.

Never solder a wire into a lug with acid flux. The flux that flows up into the wire cannot be removed.
 

Alloy

Well-known member
13.5 amps at 12v through 3 feet of #10 will have almost imperceptible voltage loss. How are you figuring a 4volt loss?

In a DC system the combined length of wire is used to calculate wire size.

My rule of thumb for runs less than 20' ( that's 10' of + plus 10' - wire) is 14ga for 15A, 12ga for 20A, 10ga for 30A.

When I'm not sure I'll use this wire calculator.
 

IdaSHO

IDACAMPER
To the OP

Just use anderson connectors.

Done right with adhesive heat shrinked wire to terminal, and you will never have a problem

Realistically the connection itself doesnt need to be weatherproof. Keeping moisture out of the wire itself is key.

Ive been using large andersen connectors (forget the amp rating) with 2awg wire for my truck to camper connection for years with zero problems.
The connection is so positive that not being weathertight is never an issue.

44094520572_84d763561a_b.jpg
 
Last edited:

john61ct

Adventurer
The thick gauge to prevent voltage drop is needed over the distance.

No harm in stepping down, via a dulal-post buss, asymmetric butt connector, ferrule, whatever.

If you just trim strands, be sure to seal the end well against corrosion, even if tinned type wire.
 

jeffjeeptj

Adventurer
I have used this SB-350 Anderson for years. It just sits under the rear bolted to the hitch. When I plug in its mate, I will plug/unplug a couple of times for cleaning. The other end of the wires in the engine compartment has a fuse and a Blue Sea ACR. I also manually connect the ACR and hook up the battery clips from my Viair for compressor duties. Been driven on salty roads in middle Tennessee, all around Florida this past winter/spring. No connection issues. It should work inside a pickup box. It connects far better than the 7 pole trailer connector. I use the SB-350 so I can use large gauge wires for voltage drop reasons.
The air connector you see is 1 of 2 for the rear airbags.521106
 

IdaSHO

IDACAMPER
I have a rear mounted andersen as well.

Its for an ATV winch, that is mounted to a crane on the firewood trailer.
Makes loading and hauling logs lengths a snap. (y)

44094522302_1e37571070_b.jpg
 

Alloy

Well-known member
Your not following.

His point is that it doesn't matter whether its AC or DC

Both consider conductor length when determining conductor size.