Way to go. I think there MAY be a GE model that looks and uses the same frame. Only issue I see is that the opening on the adapter for the controls may not be sized for the IR remote sensor. But too to know there are other options available
Mine takes a least a minute for the compressor to kick in. That pressure is probably why and/or the goverment regulates timing on high surge items as to not overload the grid after an outage. I tested my Honda 2000 on Eco Mode with the 5000 BTU unit and it ran fine on a mix of AV gas and 91. It would run even stronger on 87. My bet is with your start cap mod the tiny Honda 1000 would run one well. It probably will even run without the cap. I love my 2000 but I have plenty of space. The tiny 1000 is so light and small it would be a perfect compliment to your setup.Was able to reduce the inrush amp draw by 6A making the inrush current draw 16A down from 22. That's %37.5 decrease in amp draw averaged.
This was achieved by using a hard start kit for the compressor. Even short cycled the unit so to have high condenser pressure and the highest draw was only 18A. After running only the fan and stabilizing the refrigerant, I saw as low as 14.9 amps. Lower lift pressure for the compressor.
yeah that is why mentioned in my post that it may not be cost effective for some. Now if one is installing solar, buying batteries etc etc.... then the cost may be good cause you need less panels and batteries to run the AC..... or better said.... you might actually be able to run AC off of solar where before there was no way.The cost of a window unit that has a DC inverted compressor is 5x the cost of the walmart/home depot special compressors units.....