DaveInDenver
Middle Income Semi-Redneck
The Lincoln chart does not show a 100% duty cycle for 200A. They list a 100% duty for 400A and suggest 3/0. This agrees closely with the equations, which say 3/0 AWG for one hour at 290A will reach 150°C. A 25% derating for unforced cooling is probably appropriate.
This actually occurred to me last night in class. I'm doing SMAW in the current welding school cycle (continuing education requirements). They use 2 AWG cables on the welders (Lincoln Invertec 275 funny enough). Noticed the leads were getting warm doing 7018 at 125A after a couple of hours. Of course showering them with slag probably doesn't help at all. I'm not pushing 100% duty with swapping rods and periodically cooling the bead plate.
This actually occurred to me last night in class. I'm doing SMAW in the current welding school cycle (continuing education requirements). They use 2 AWG cables on the welders (Lincoln Invertec 275 funny enough). Noticed the leads were getting warm doing 7018 at 125A after a couple of hours. Of course showering them with slag probably doesn't help at all. I'm not pushing 100% duty with swapping rods and periodically cooling the bead plate.